• PID controller with a limited range of control variable

    From pozz@pozzugno@gmail.com to comp.arch.embedded on Wed Apr 26 08:57:08 2023
    From Newsgroup: comp.arch.embedded

    In one application an AC voltage sourced by a generator is applied to a
    load as a PWM waveform. The period PER is fixed (for example, 100ms) and
    the pulse-width PW has a maximum (for example, 20ms).

    The user can change the voltage peak (and consequently the voltage RMS)
    by an handle, while the controller manages automatically the PW.

    The load changes its temperature when the PWM waveform is applied to it
    and a sensor that read the temperature is present.

    There's a temperature upper limit (for example, 40°C) that mustn't be exceeded. If needed, the controller should decrease the PW accordingly
    to avoid temperature overshoot. Otherwise, the PW is the maximum allowed (20ms).

    Of course, when the voltage peak is low, PW could be the maximum. When
    the user increases the voltage, the controller should be smart enough to reduce PW accordingly and fast to avoid temperature overshoot.

    I was thinking to implement a PID controller with the load temperature
    as the process variable PV and the thermal power as the control variable
    CV. From the thermal power I could calculate the PW to use.

    CV = Vrms^2 / Z * PW / PER

    Apart calibrating the PID constants, there's another problem. When the
    voltage is low, the CV from the PID algorithm would be greater than the maximum allowed (limited by PW maximum duration). The system could stay
    in this state for minutes, so the PW calculated by the PID assumes very
    great values with time.

    When the user decides to increase the voltage and there's the moment to
    reduce the PW, the PID behaviour could be very slow, because it would
    start from a very high PW (very high sum of errors of the integrative part).

    What's the trick here to avoid this behaviour? Should I limit the sum of errors of the I term? Should I re-initialize the PID state in some way?
    --- Synchronet 3.20a-Linux NewsLink 1.114
  • From Ed Prochak@edprochak@gmail.com to comp.arch.embedded on Thu Apr 27 14:14:00 2023
    From Newsgroup: comp.arch.embedded

    On Wednesday, April 26, 2023 at 2:57:14 AM UTC-4, pozz wrote:
    In one application an AC voltage sourced by a generator is applied to a
    load as a PWM waveform. The period PER is fixed (for example, 100ms) and
    the pulse-width PW has a maximum (for example, 20ms).

    The user can change the voltage peak (and consequently the voltage RMS)
    by an handle, while the controller manages automatically the PW.
    Looks like an unusual feature to me. Can you share what the purpose of varying the supply voltage?

    The load changes its temperature when the PWM waveform is applied to it
    and a sensor that read the temperature is present.

    There's a temperature upper limit (for example, 40°C) that mustn't be exceeded. If needed, the controller should decrease the PW accordingly
    to avoid temperature overshoot. Otherwise, the PW is the maximum allowed (20ms).

    Of course, when the voltage peak is low, PW could be the maximum. When
    the user increases the voltage, the controller should be smart enough to reduce PW accordingly and fast to avoid temperature overshoot.

    I was thinking to implement a PID controller with the load temperature
    as the process variable PV and the thermal power as the control variable
    CV. From the thermal power I could calculate the PW to use.

    CV = Vrms^2 / Z * PW / PER

    Apart calibrating the PID constants, there's another problem. When the voltage is low, the CV from the PID algorithm would be greater than the maximum allowed (limited by PW maximum duration). The system could stay
    in this state for minutes, so the PW calculated by the PID assumes very great values with time.

    When the user decides to increase the voltage and there's the moment to reduce the PW, the PID behaviour could be very slow, because it would
    start from a very high PW (very high sum of errors of the integrative part).

    What's the trick here to avoid this behaviour? Should I limit the sum of errors of the I term? Should I re-initialize the PID state in some way?
    I think the easiest solution is to cap the error/PW value.
    Good luck,
    Ed